Hello, Please have a look on the following FAQs: How can you report S7 system errors in WinCC? and How can you have system error messages from a SIMATIC S7-300 / 400 displayed in WinCC flexible? Regards, |
Last edited by: Ayman Elotaify at: 6/30/2009 8:19 AMAyman Elotaify |
|
6/30/2009 8:28 AM | |
Posts: 160 Rating: (16) |
Use the standard function SFC51 with SSL_ID #174. Have a look in the online help for this block but this is exactly what you are after. |
6/30/2009 9:07 AM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309) |
Hello Baher, Mumbles' solution is the only thing I know for what you want. A detailed example can be found here. Just download the example named Getting the Status for the CPU LED Indicators. Best regards. H-H |
This contribution was helpful to1 thankful Users |
6/30/2009 6:13 PM | |
Posts: 18 Rating: (1) |
Thank you All. It worked with the SFC 51. Thanks, Baher |