Dear all, May some one please advice me on what is the maximum concurrent communcation can be established by CP343-1 (6GK7 343-1EX30-0XE0). Lately i added in the above mentioned card on my CPU 315-2 DP rack to connect the mentioned system to plant SCADA system (Proficy i-Fix system) with redundent server. However, it seems like the CP343-1 is not capable to form 2 concurrent connection at the same time. The redundent (secondary server) always failed to establish connection with CP343-1. Once i shutdown primary server, the connection at secondary back to online (network established). My question is, is there any setting can be done to increase the concurrent connection? Any other possible way to improve the system? Upgrade the CPU/CP? Please advise. Thanks in advance. Regards Sean
AttachmentmoduleInfo.zip (62 Downloads) |
9/23/2014 9:14 AM | |
Posts: 1368 Rating:
|
Hello, the CP can manage up to 16 connections parallel, so this can not be the mistake... I think, the communication to HMI via OPC is an open communication.... Have a look at this overview http://support.automation.siemens.com/WW/view/de/16767769 Do you have any connections over CPU? |
Last edited by: Pittiplatsch at: 9/23/2014 9:16 AM |
|
9/25/2014 7:23 AM | |
Posts: 11 Rating:
|
Hi Pittiplatsch, I have Profibus DP network on the CPU. 3 remote I/O station attached on the above mentioned network. Regards sean
|