Hi Friends, i need information about siemens CPU 315 2 PN/DP Can i configure 5 Robotic controller (Yaskawa), 5 timming control unit (weld controller), 6 valve bank (SMC module), 4 remote i/o (such as Siemens IM151-1), 4 spare romote i/o, 4 HMI (SIEMENS TP1200 Comfort), 2 Drive (may be Siemens or allen bradley) by using PROFINET. this is possible in CPU 315 2 PN/DP (6ES7 315 2EH14 0AB0) , if is it not possible then which PLC support this configuration? Thanks & Regards Achal Borke ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 4/15/2016 2:07:38 PMNew subject after splitting |
|
4/15/2016 5:01 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello Pl go through the Technical data of CPU 315-2PN/DP
a) The complexity of application ( Estimated program size ) ? |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
4/18/2016 8:24 AM | |
Posts: 2 Rating: (0) |
also i need to know how many HMI (TP1200 SIEMENS) Communicate with 315 2PN/DP PLC And there is any effect on S7 communication |
4/18/2016 10:34 AM | |
Joined: 3/3/2014 Last visit: 7/22/2024 Posts: 234 Rating: (9) |
By profinet, you can connect up to 128 devices. |
Last edited by: sbartoc at: 4/18/2016 10:34:58 AM |
|
4/18/2016 11:35 AM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Yes you can connect upto 128 PROFINET devices. However HMI panel is considered as a OP Device and occupies communication resources accordingly. Pl See Attached Datasheet - Page-14 ( Connections usable fro OP Communication ) AttachmentS7300_CPU315_2PNDP_6ES73152EH140AB0_en.pdf (322 Downloads) |
Last edited by: Navnag at: 4/18/2016 11:36:19 AMLast edited by: Navnag at: 4/18/2016 11:37:42 AMLast edited by: Navnag at: 4/18/2016 11:38:19 AMThere is no such thing as the last bug in a program |
|
This contribution was helpful to2 thankful Users |
4/18/2016 11:13 PM | |
Joined: 5/28/2008 Last visit: 9/9/2024 Posts: 4515 Rating: (839)
|
Hello, As Nannag said, Max. is 16. What is the maximum number of OPs that a CPU S7-300 can communicate with? |
Ayman Elotaify |
|
6/30/2017 9:42 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by vipz is split to a separate thread with the subject How the resources of HMI is calculated?. Best regards |