Dear Engineer.. Attachment315_2DP_Diggnositc_buffer.pdf (429 Downloads) |
9/15/2009 1:34 PM | |
Joined: 4/24/2006 Last visit: 9/10/2024 Posts: 8736 Rating: (1167) |
Dear Moong, You can try to do the following. Switch to MRES and hold for 9 seconds, then release Switch MRES. But within 3 seconds Switch it back to MRES and hold for at least 5 seconds. See also this link: http://support.automation.siemens.com/WW/view/en/21830698 Best regards, Wizard |