Industry Online Support
Technical Forum
9/6/2011 11:33 AM | |
Posts: 3 Rating: (0) |
Hi, I have CPU 315. When power fails and then restores then SF LED comes ON. PLC stays in RUN mode. Simocodes and power monitor connected on CPU DP port. Some simocodes stays in General Fault due to trip conditions (Thermister). If the simocode fault is cleared then SF LED goes OFF. Attached the diagnose file. Buffer mentions Rack failure during startup (03:20) When the node faults (Simocode) are cleared (03:40) the SF LED goes OFF. Diagnostic buffer entry shows Hardware interrupt interrupt line 1. Question is: 1. Does the SF LED turns ON if any node on DP port is in fault condition? AttachmentDiagnose.zip (180 Downloads) |
9/8/2011 8:27 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Yes, this is true. SF LED plus BF LED are ON. In case if there aren't downloaded "error" OBs the CPU does in STOP. Best regards, Hristo Mihalev |
This contribution was helpful to1 thankful Users |