6/6/2014 3:30 PM | |
Joined: 9/27/2006 Last visit: 9/30/2023 Posts: 12153 Rating:
|
Hello rjdobler; The first step to add a Wago slave (or a Profibus slave from any manufacturer) to a Siemens DP master is to integrate the Wago 767 GSD file in the HWConfig editor: See the corresponding description in the 767 datasheet: 767-1101; FC PROFIBUS DP 8DI 24V DC - Wago --- the coupler provides the connected I/O modules with the parametrization data provided by the device description (GSD file) and transferred by the DP master… You should find the 767 gsd fle in the following link from Wago: GSD files for PROFIBUS with installation program Once you have the file unzipped in your computer, open the HWConfig editor of Simatic manager, but with a little twist: there must be no open project in HWConfig (you must see a blank window); then iou canuse the menu Tools/Import gsd file, so the slave will appear somewhere in the Profibus catalog (generally in "Other slaves"). When you want to configure a new 767-1101slave simply drag one from the catalog onto the Profibus line of the CPU, give it a Profibus address (unique for the network) and you should see the modules of your slave appear in the bottom part of the Profibus configurator (if needed you can add new modules with different carateristics), with I and Q adresses that you can use directly in your program. For Safety IOs, once configured, your Safety program (developped through the Distributed Safety software package) can access these addresses also, through a mechanism called Distributed Safety that is transparent to the user. This should give you a headstart, please come back to the forum if you need more information or if you face some problems. Hope this helps, Daniel Chartier |
This contribution was helpful to
3 thankful Users |
6/11/2014 3:46 PM | |
Posts: 5 Rating:
|
Hello Daniel, how are you? Thank you for your answer! We did the configuration of the Wago slave with the CPU 319F using the Step 7 Software and the GSD File from Wago. The WAGO slave has these modules: 750-333 + 750-626 + 750-432 + 750-530 + 750-660 + 750-665 + 750-600. With the Wago I/O check software (by USB), we could get the Wago configuration Information, but we could not access it by the CPU. Now, we are having some problems with the CPU LEDs, which are indicating some erros. Could you please look at the the attached zip file, which contains some pictures of the system and Step 7 information? Maybe we did something wrong during the setup. The CPU show errors for the LEDS: SF (red) and BF 2 (red and blinking or flashing). We are not being able to solve them...Sorry if our questions seams dumb, but we have no experience with the automation area yet, we just begining in this area. Thanks a lot for your help and patience in helping us. Best regards, Rodrigo. AttachmentPictures = Step 7 and the system.zip (212 Downloads) |
6/19/2014 7:57 AM | |
Posts: 5 Rating:
|
Hello TEBANCH and Daniel Chartier! We were able to setup the CPU 319F with the Standard PROFIBUS modules from wago. I took some pictures from the system and included them with the message. The problem is still with the PROFIsafe modules...with them, we are no being able to setup the CPU and the Wago I/O module (same problems with the LEDs SF andBF2). We will keep working to solve then...but at least now we know that the GSD file, cables are working correctly. I think that we need to solve some configuration problem with the PROFIsafe modules. Best regards, Rodrigo.
AttachmentStandard Wago PROFIBUS modules.zip (235 Downloads) |
7/2/2014 10:04 AM | |
Posts: 5 Rating:
|
Hello!!! Now we were able to setup the CPU 319F + the Wago I/O modules.
The mistake made by us was with the PROFIsafe address in the module's proporties at Step 7. We had already setup the PROFIsafe address using the DIPSwitches at each PROFIsafe module. We were no putting 1021 and 1022 for the PROFIsafe destination address and this was the problem. It was a stupid mistake that consumed a lot of time and effort...but at least we did it. Lack of experience sometimes is a problem The attached file shows the pictures of Step 7 and the real system. Now there is no more Leds indicating errors. I would like to ask if someone has a code (STL language) that acess the inputs and outputs of a module (or modules) just to serve as an example for us to start. Thanks a lot and best regards, Rodrigo. AttachmentWorking Setup.zip (231 Downloads) |