7/23/2010 10:22 PM | |
Joined: 9/27/2006 Last visit: 5/19/2024 Posts: 12257 Rating: (2668)
|
Hello Abdo; The LEDs are simply saying that you should open the diagnostic buffer and look at what the CPU is complaining about. The LEDs indicate that you have an internal fault (fault inthe CPU, such as a programming error or a watchdog timer overrun), an external fault (diagnostic fault on a module or in the rack) and a remote module (Profibus) error. But for details you should open the diagnostic buffer. If you need help decyphering the cointents of the diagnostic buffer copy the relevant entries here, we wiil try to help. For details on the diagnostic LEDs, have a look at the S7-400 CPU Specifications manual: http://support.automation.siemens.com/WW/view/en/14016796 Hope this helps, Daniel Chartier |
7/23/2010 11:14 PM | |
Posts: 99 Rating: (0) |
thanks regarding the indicator led i know what each one means. but the thing here is my CP443-5 module is swoing no error its working fine and my system is working fine as well. in the HW config, the CP module is showing the error sign although the module itself is ok. when i put the diagnostic buffer it shows on of the message that the max diagnostic data length can be evalouated please advise me thanks |
8/8/2017 7:51 AM | |
Joined: 6/19/2017 Last visit: 5/17/2024 Posts: 8034 Rating: (164) |
New question published by babblu arrja is split to a separate thread with the subject Not able to complete download - Error 2000 and 120 occured. Best regards |