12/29/2016 5:29 PM | |
Posts: 3093 Rating:
|
Hello Ricci Allen, Regards, |
12/29/2016 5:44 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, That leaves 118 connections in total (if you don't have more PGs and HMI connected). The integrated Profinet port seems to support up to 118 open IE. Be aware that redundant systems perform synchronization between CPUs each time received data may cause the two CPUs to compute different results. In other words, communication will increase the cycle time more than in a non redundant system. Would be nice that the technical expert from this conference can confirm my understanding. |
Last edited by: jklm at: 12/29/2016 5:46:28 PMBest regards |
|
This contribution was helpful to
2 thankful Users |
12/29/2016 7:28 PM | |
Posts: 3 Rating:
|
Thanks jklm, that is very helpful and the link was great added touch. |
12/30/2016 12:21 PM | |
Posts: 3093 Rating:
|
Hello jklm, Regards,
|