3/19/2009 1:21 PM | |
Joined: 10/9/2007 Last visit: 7/10/2025 Posts: 1273 Rating:
|
Hi All Take a look at www.siprotec.com. On the left panel click on Protection Devices and then choose your device. In the central panel look at the bottom of the page and you'll find the Mapping Files for Profibus DP. Generally they offer some variations for this mapping file (the difference is the quantity of informations which can be transferred), but it is not dependentto MLFB. Maybe changing MFLB you add/remove protection functions, then maybe you have to use another variation (called Standard Mapping in Siprotec manuals). Take a look at this example: http://siemens.siprotec.de/download_neu/devices/1_General/Doku_Protokolle/Englisch/Profibus%20DP/Profibus_DP_with_SM_3-1_since_3-n/com_profibus_7sj6x_6md63_us.pdf And remember that Profibus FMS is available only for use together with Sicam PAS and Sicam SAS, substation automation solutions from Energy sector from Siemens. Regards Mike J |
Energy Automation products: Sicam, Siprotec, Digsi |
|
3/19/2009 1:39 PM | |
Posts: 38 Rating:
|
Thanks alot for all your help. I will definately take a look at that example. I am pretty sure I will have to change the MLFB, might as well be safe. Thanks |
3/19/2009 2:42 PM | |
Posts: 38 Rating:
|
Yes, when I say SAS I am using SICAM SAS. The communication is done through Profibus FMS connection. |
Follow us on