4/7/2014 2:04 PM | |
Posts: 27 Rating: (0) |
Hello experts I'm new with Siemens step5 and I've got plc S5 100-u. I encountered problems with my simple program with two blocks OB1 and FB32. While downloading program to the cpu, plc goes into stop. I dont know whats the reason of this situation because I tried to write the pogram according to the siemens manual. Can anybody help me to understand it? regards AttachmentHYGIENST.zip (229 Downloads) |
4/9/2014 3:32 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello gregory245 As per the program logic you should have a DI Module in Slot-0 ( Address I0.0 .. ) and a DO Module in Slot-1 ( Address Q 1.0 .. ).Have youinstalled and wired these modules ? Is the Ribbon cable of the Bus Module ( On which I/O Modules are mounted ) plugged into the CPU ? Are the DI/DO Modules powered up ? Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
4/9/2014 4:38 PM | |
Posts: 27 Rating: (0) |
Of course everythink is wired properly and ribbon cable is also plugged into the cpu. When I create a program in OB1 block only, then everythink works properly. The problem comes when FB's are loaded into plc. STOZUS and STOANZ control bits are active. |
4/9/2014 4:48 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello gregory245 Can you post the screenshots of ISTACK+ Cause of interrupt and BSTACK here for understanding the problem. Cheers Navnag |
Last edited by: Navnag at: 4/9/2014 4:52 PMThere is no such thing as the last bug in a program |
|
4/9/2014 5:16 PM | |
Posts: 27 Rating: (0) |
here's Istack and Bstack screenshots regards AttachmentSTACKS.zip (247 Downloads) |
4/9/2014 8:53 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Which is the CPU Type that you are using ? Please note that The FB with Formal Operands are only permitted in CPU 103 and not in CPU 100 / CPU 102 of the 100U Series. If you use these commands in CPU 100 / 102 then it will g to STOP Mode with error "NNN" in ISTACK Please see attached extract from the manual to see which commands are permitted in which CPUs. Hope this helps Cheers Navnag Attachment100U_Formal_Operands.pdf (254 Downloads) |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
4/10/2014 8:30 AM | |
Posts: 27 Rating: (0) |
Thanks Navnag for explanation I use cpu 100 and that's why I couldn't be able to download my program. greetings |
This contribution was helpful to1 thankful Users |