6/29/2017 12:07 PM | |
Joined: 2/4/2015 Last visit: 12/28/2024 Posts: 67 Rating:
|
Hi all, I am having a S7-400H CPU 416-5HS06-0AB0. From the PN port i have connected an IM-153-4BA00-0XB0 through ethernet cable. I have set the IP and name of IM. downloaded the hardware to CPU. Now the CPU went to Run mode but IM is not ready yet.Bus fault is blinking. What may be the problem? Kindly help. I have not placed the memory card. Is it needed? Regards Surendhar M ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 6/30/2017 10:57:29 AMNew subject after splitting |
|
6/29/2017 1:24 PM | |
Joined: 2/4/2015 Last visit: 12/28/2024 Posts: 67 Rating:
|
Hi Mr.Christoph, PFA Regards Surendhar M AttachmentHardware.zip (125 Downloads) |
6/29/2017 1:26 PM | |
Joined: 2/4/2015 Last visit: 12/28/2024 Posts: 67 Rating:
|
Hi, PFA Regards Surendhar M AttachmentDiagnostics.zip (119 Downloads) |
6/29/2017 1:41 PM | |
Joined: 2/4/2015 Last visit: 12/28/2024 Posts: 67 Rating:
|
Sorry for the wrong attachement PFA Regards Surendhar M AttachmentEdit Ethernet Node.zip (132 Downloads) |
6/29/2017 1:58 PM | |
Joined: 2/4/2015 Last visit: 12/28/2024 Posts: 67 Rating:
|
Hi Mr.Christoph, Thanks. Changed the name. Now its communicating Thank u so much. Regards Surendhar M |