4/12/2013 7:58 AM | |
Posts: 7 Rating: (0) |
Dear Support, Currenlty usedS7 215 PLC Part # 6ES7-215-2BD00-OXBO these are used as a remote I/O for each SCR cubile with Profibus Interface with S7 315 PLC(Enclosed topology for reference) Unforutely we areexperiencingSCR3 cubicle CPU215becomes stopmode indication(It was happensrandomly sometime before,Electrician was restarted becomes normal).Now we have Informed from Electrician the this becomesperament stop mode Indication.It was understood,This product order code number was not tracble from Siemens website,Please advise how this can be resolved. System was deliveredmore than 10years old and Vendor is not tracable,Please review and easiest recommendation toreplacment solutions and advise Best Regards Partha AttachmentWA_Profibus _Network actual Installation.pdf (29 Downloads) |
Last edited by: O_Moderator at: 4/12/2013 8:02 AM |
|
4/12/2013 8:26 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (713)
|
Hello, Logical start is to read the PLC error with Microwin, error discription is in this manual. the 215 system is in it too. In case of hardware failure, you can replace the PLC by i.e. CPU 224, AC PS, 14DI DC/10DO RELAY And add a profibus module: PROFIBUS DP SLAVE MODULE, 9.6KB - 12MB There have to be made some changes in the S7-300 PLC. Regards, Marcjan |
Last edited by: Marcjan at: 4/12/2013 4:23 PMLast edited by: Marcjan at: 4/12/2013 9:09 AMLast edited by: Marcjan at: 4/12/2013 8:31 AMProblem solved? |
|