7/3/2009 12:59 PM | |
Posts: 34 Rating: (2) |
hi attached is the siemens document reference in this document it is mentioned, DB800 has to be created in siemens CPU but i am having CPU313c-2dp, which is having limit of DB511 regards dilipan AttachmentCP341.pdf (160 Downloads) |
7/3/2009 2:40 PM | |
Joined: 10/7/2005 Last visit: 1/17/2025 Posts: 3030 Rating: (1058) |
Dear dilipan_c no need to worry, its just a simple matter of misreading the "example" in the CP341 Modbus Slave manual (which is just what the name suggest: An example. Mind you, one could argue that Siemens would create examples that use DB numbers which are supported in all CPU's). You can use ANY DB as the so called "Base DB" for the Modbus Function codes 3 (Read multiple Registers), 6 (Write single Register) and 16(Write multipleRegisters). Which DB you want to use as the "Base DB" isdeclared in the Poin to Point parameterisation of the Modbus Slave Driverfor the CP341 and the attached screendump hopefully "saysmore than a thousands words" (DB100 is declared as the Base DB for Modbus FC 3,6&16 in this "example"). I hope this helps P.S:Apologiesfor the German in the screendumps, my installation is in English but this is not the first time Siemens "forgot" to translate screens. |
Cheers |
|
This contribution was helpful to1 thankful Users |
7/3/2009 4:01 PM | |
Posts: 34 Rating: (2) |
thanks chartier and fritz
excellent reply regards dilipan |