8/29/2011 1:12 PM | |
Posts: 103 Rating: (0) |
dear experts i wanna know that the cpu 313c-2dp supports the process image or not, to read the analog input through profibuus adaptor module (RPBA-01) thanks |
8/29/2011 1:21 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello, Yes, it supports PIP. Just the number of process image partitions available depends on the CPU used! Take a look at http://support.automation.siemens.com/WW/view/en/18325417 In order to read from Profibus slave there use a SFC14 and SFC15. Best regards, Hristo Mihalev |