1/29/2010 8:05 AM | |
Posts: 21 Rating:
I forgot to say that the AI worked fine, so I don't think that there is a need for other devices. |
1/29/2010 4:36 PM | |
Joined: 7/2/2008 Last visit: 9/14/2023 Posts: 928 Rating:
Hello Donflore, I've experienced a faulty channel in 314IFM with fixed reading value but other channels were working fine. You said that the AI signals worked fine but they give you the same value now even if they are not wired. Create and download a new projectand check the suspected channels again in case they are wired and in case they are not. If the values of peripheral analog inputs are still fixed (21500 dec.) without a change then it looks like you have defective AI channels. Best regards. H-H |