7/26/2013 12:36 PM | |
Posts: 68 Rating:
|
Dear all I having CPU317PN/DP with ET200M IM153-2 In this Replace the modules during the operation possible or not. |
7/26/2013 2:04 PM | |
Joined: 4/24/2006 Last visit: 11/27/2023 Posts: 8596 Rating:
|
Hello S5 SHOOTER, You mean Hot-Swappable? Best regards, Wizard |
7/26/2013 2:15 PM | |
Joined: 9/27/2006 Last visit: 11/28/2023 Posts: 12176 Rating:
|
Hello S5 shooter; CiR (Configure in Runtime) is a function that allows swapping of slave modules without stopping the DP master operations. The manual for CiR can be found here: SIMATIC STEP7 V5.5 Modifying the System during Operation via CiR |
Last edited by: O_Moderator at: 7/26/2013 2:19 PMattachment reattached |
|
This contribution was helpful to
1 thankful Users |
7/26/2013 3:03 PM | |
Posts: 68 Rating:
|
Hello Wizard, Yes I need Hot Swapping Only .This Possible CPU317PN/DP with ET200M 153-2 What are the setting have do in Hardware configuration Best Regards, |
7/26/2013 3:18 PM | |
Joined: 4/24/2006 Last visit: 11/27/2023 Posts: 8596 Rating:
|
Please have a look at this thread: /tf/WW/en/Posts/33828 And a look at this thread: /tf/WW/en/Posts/3357 If your CPU can handle OB83, it might work. (For ET200M you need the Active backplane) And this link: "Module change during operation" - Configuration and system requirements Best regards, Wizard |
Last edited by: Wizard at: 7/26/2013 3:28 PM |
|