3/27/2014 5:51 AM | |
Posts: 57 Rating: (0) |
Hi Everybody, Can anyone guide me with the basic parameter settings for crane application(HOIST) with Sinamics S-120 drive CU320-2DP. Thanks
|
3/31/2014 11:46 AM | |
Joined: 10/11/2006 Last visit: 4/23/2024 Posts: 5821 Rating: (789)
|
Hello, this depends on your requirement. Is it speed controlled only, or do you need a drive based positioning? Do you calculate the speed / positionsetpoint in a superimposed PLC? Do you have a gantry application - each motor has a own motormodule? Is it a wheel / rail system? I recommend to contact your SIEMENS partner: https://www.automation.siemens.com/mcms/aspa-db/en/drive-technology/Pages/default.aspx?HTTPS=REDIR |
With best regards, |
|
4/14/2014 2:27 PM | |
Posts: 57 Rating: (0) |
Hi Everybody, Does anybody have any back-up of crane application with brake logic with Sinamics S-120 Drive CU320-2DP and PM 340. Plz reply Thanks
|
5/17/2019 3:30 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating: (67) |
Yes for cranes you can use SINAMICS. Also Motors for Cranes are available. |
5/18/2019 10:17 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Below links may help you. AP13: SINAMICS S120 SLM Sizing and Configuration for Cranes AP12: SINAMICS S120 Calculation of converter losses at partial load SINAMICS S120: Handling the 'Safe Brake Test' (SBT) in conjunction with the EPOS function AP07: Power cycling capability of IGBT modules and power units (Information for Cranes Settings AP05: SINAMICS S120 Insulation monitoring on cranes |
Last edited by: PISCEAN 2010 at: 05/18/2019 10:21:52Last edited by: PISCEAN 2010 at: 05/18/2019 10:29:34Last edited by: Jen_Moderator at: 05/20/2019 10:09:36Optimized links. |
|
This contribution was helpful to2 thankful Users |
5/20/2019 7:20 AM | |
Joined: 9/3/2018 Last visit: 4/15/2024 Posts: 26 Rating: (0) |
|