12/6/2017 2:36 PM | |
Posts: 1368 Rating: (126) |
If you change the operating mode of PLC to "IO device", you can export GSD file of PLC. Perhaps this way works.... Greetings |
12/8/2017 6:19 AM | |
Joined: 5/12/2006 Last visit: 4/24/2024 Posts: 22226 Rating: (2980)
|
Hello, this is documented in the technical data of the PLC. https://support.industry.siemens.com/cs/ww/en/pv/6ES7516-3AN01-0AB0/td Regards |
This contribution was helpful to2 thankful Users |
12/8/2017 7:05 AM | |
Joined: 8/5/2014 Last visit: 4/10/2024 Posts: 158 Rating: (4) |
Hello, I checked with 315-2PN/DP(6ES7315-2EH13-0AB0), when i selected DP Slave then Export option for GSD is not available, then how to create GSD file?
|
Regards, |
|
12/8/2017 7:09 AM | |
Joined: 5/12/2006 Last visit: 4/24/2024 Posts: 22226 Rating: (2980)
|
Hello, For S7-300 or some Other PLC/CP with DP-Slave you can download the GSD File in SIOS. https://support.industry.siemens.com/cs/ww/en/view/113652 GSD is not based on XML so a generic Export like PROFINET GSDML File is not available! Regards Christoph |
This contribution was helpful to1 thankful Users |
12/8/2017 7:17 AM | |
Joined: 8/5/2014 Last visit: 4/10/2024 Posts: 158 Rating: (4) |
Thank you for your precious time.
|
Regards, |
|