5/13/2022 9:55 AM | |
Joined: 12/13/2016 Last visit: 2/16/2025 Posts: 15 Rating:
|
Help me please I was ploblem S7-1200 CPU1215C DC/DC/DC Motion control via CU 250S 2-PN G120 Drive Develop TIA V17 occurred Axis error while motor running until 30 minute I attach file for explain How can i do fix it case.? Thank you every body AttachmentFiles.zip (539 Downloads) |
Last edited by: Jen_Moderator at: 05/13/2022 11:52:06Added all files as a zip file. |
|
5/16/2022 11:05 AM | |
Joined: 11/4/2011 Last visit: 2/17/2025 Posts: 257 Rating:
|
Hi there, basically RB91 has already said anything there is to say. You have a following error, i.e. the actual values cannot follow your setpoint values good enough, and therefor the following error monitoring has thrown this alarm, as configured. Here you can find some background on the following error monitoring: https://support.industry.siemens.com/cs/de/en/view/109773400/124327761291 Short note: do NOT just disable the following error montoring, in order to get rid of the error. This will not solve anything but only hide the issue (which might result in other issues then that might be worse). What you need to do is to check the following:
For drive optimization see this FAQ (even though this refers to S120, S210 and V90 I'm sure you can still adapt the procedure to your G120): https://support.industry.siemens.com/cs/de/en/view/60593549 You might also check this application example, to get an idea of how to optimize the TO: https://support.industry.siemens.com/cs/de/en/view/109479977 Regards, |