1/10/2018 10:44 PM | |
Joined: 9/8/2009 Last visit: 7/17/2023 Posts: 1410 Rating:
|
What kind of macro you are referring at? |
1/11/2018 5:04 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello harry998, Set P0015 = 103 to activate "pump pressure control" macro. Please refer attached sheet for more information. AttachmentCU230P_Pump pressure control.pdf (194 Downloads) |
1/11/2018 8:15 AM | |
Posts: 14 Rating:
|
Hi Piscean, that is what im trying to do but it doesn't accept it, it only gives me 5 or 6 options. I will take a screen shot and post. Thanks, Harry |
1/11/2018 8:50 AM | |
Posts: 14 Rating:
|
|
1/11/2018 9:09 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Check CU230P - DP version. It should be 4.4. Check below FAQ for more information. SINAMICS G120/G120P, CU230P-2: Pressure-Controlled PumpsHTH. For CU230P-PN with FW version 4.6 SP6 refer below FAQ, download example, refer page 33, 39, 45 SINAMICS G120 converter with Control Units CU230P-2; CU240B-2; CU240E-2 |
Last edited by: PISCEAN 2010 at: 1/11/2018 9:25:18 AMLast edited by: PISCEAN 2010 at: 1/11/2018 9:27:42 AMLast edited by: Jen_Moderator at: 1/19/2018 2:10:28 PMInserted right links. |
|
1/11/2018 8:58 PM | |
Posts: 14 Rating:
|
I have used the second manual you attached to try and solve the problem but no luck, i will double check the firmware version tomorrow though just to be sure. Even if i try too manually map the settings to match the macro description some options are not there for instance AI0 to r 0755 is not an available option?! Its really looking like a lot of the optional macros are missing from the control unit? Thanks, Harry AttachmentCU230P-2 Control Units.pdf (193 Downloads) |