5/6/2013 7:32 PM | |
Posts: 767 Rating: (69) |
Hello nandgate, Following is the description of the fault mentioned. F30001 Overcurrent Check the following: Motor data, if required, carry out commissioning Motor connection method (Υ / Δ) U/f operation: Assignment of rated currents of motor and PowerModule Line quality Make sure that the line commutating reactor is connected properly Power cable connections Power cables for short-circuit or ground fault Power cable length Line phasesIf this doesn't help: U/f operation: Increase the acceleration ramp Reduce the load Replace the power unit |
5/16/2013 1:41 PM | |
Posts: 319 Rating: (9) |
Thank you all for your valuable support. |