9/14/2020 1:49 PM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating: (301) |
Hi, I would highly recommend to do it this way... Use standard telegram 352 and add supplementary data as a new telegram slot. This brings the advantage that you have one separate slot and Hardware ID for telegram 352 and you can use the SINA_SPEED FB from the LSinaExt library to control the drive in a simple way from your PLC program - find the lib here: https://support.industry.siemens.com/cs/de/en/view/109747655 The added supplementary data gets its own Hardware ID (address to PLC) so you can read that data from your PLC program for example by using the GETIO function. So add 2 supplementary words to your drive. To the first one you connect the DI in one bit and in the second word you connect the AI value of the sensor. |
Best regards, |
|
This contribution was helpful to1 thankful Users |
9/14/2020 2:37 PM | |
Joined: 7/7/2010 Last visit: 1/21/2025 Posts: 15549 Rating: (2465) |
I had better luck with the link given like this: https://support.industry.siemens.com/cs/document/109747655
|
science guy |
|
This contribution was helpful to1 thankful Users |
9/14/2020 3:11 PM | |
Joined: 7/7/2010 Last visit: 1/21/2025 Posts: 15549 Rating: (2465) |
You will want to select parameters from the Control Unit, not the drive object with the motor module. |
science guy |
|
9/14/2020 3:50 PM | |
Joined: 9/8/2016 Last visit: 12/10/2024 Posts: 198 Rating: (10) |
When i activate button (red marked) the parameters list show up (uploaded in prevoius posts). |