3/22/2018 3:02 PM | |
Posts: 33 Rating: (0) |
I make all steps above withe commssining cu with startar onnly but after loading program on Cu320 give alarm and lamp for ready giving read |
3/22/2018 3:06 PM | |
Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015)
|
Hello, and which alarm/fault ? Christoph |
3/22/2018 3:24 PM | |
Posts: 33 Rating: (0) |
The picture for control unit rem is the same control unit |
3/22/2018 3:30 PM | |
Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015)
|
Hello, ok this is the old CU320 . Which FW Version you use? Which Fault you get ? Regards Christoph |
3/22/2018 3:31 PM | |
Joined: 5/28/2008 Last visit: 10/4/2024 Posts: 4515 Rating: (839) |
Hello, You can begin with the following manuals: SINAMICS S120 Getting Started with STARTER SINAMICS S120 Commissioning Manual with STARTER But it will be highly recommended to call a Siemens representative experienced with Starter for comission your application (at least for the first time). Hope this helps. |
Ayman Elotaify |
|