8/14/2014 12:27 PM | |
Posts: 10 Rating:
|
Hi, I am starting to work with scripts in Tia Portal v12 for program my TP1200 and I dont find a basic feature of scripting for these panels. I need a cyclic script to check the status of a variable. For this I am using a clock variable of a PLC (1hz) for run the script in the "Value Change". But the script dont work. For test if i made a mistake in the programming of my script I created a button that runs this script in the "click". However here it works right. I have a similar problem as the guy ofthis thread, but with WinCC Confort (here I dont have "Global Script Runtime" ). How can I run a script cyclically? Thanks.
|
8/14/2014 12:48 PM | |
Posts: 1299 Rating:
|
Hello, how did you set the aquisition cycle of theclock variable? If it's "on demand" and you don't use it in the picture it won't work. K!ke |
8/18/2014 8:45 AM | |
Posts: 10 Rating:
|
Thanks Brain!! This works for me. |