Joined: 1/25/2012 Last visit: 9/19/2024 Posts: 7 Rating:
|
Hello i have a problem and i have no idea to solve it at the moment. I have a Simotion D435-2 which is communicated by industrial ethernet with a PC677. It is running well since 3-4 years. Until i made some modifications in the Simotion and after "compile modifications" and reloading, the hmi no more display the values of the simotion (#####) i just could see on the alarm view fault 140020 which says data of the cpu and data of the hmi are not in the same versions. I think there is something the hmi consistency check. i read in the documentation that a data for the consistency is generated by scout which is used at the starting of wincc flexible. I think this data is not consistent and so the communication don't start. that's my idea. I try different tests save and compile modifications/save and compile all then reload simotion. with wincc flexible open during compilation, then i try with wincc flexible close, open after simotion reloading..nothing works.. I just have a (before modifications) version of the project. If i load both of cpu/hmi it works again.. If someone can give me an idea about making both simotion/hmi consistent and communicating Thanks (the simotion/hmi settings are in a pdf file attached) My configuration Scout classic 4.5/Wincc flexible 2008 sp3 runtime PC/Step7 5.5 Sp4 hf11 Wincc project is integrated in Step7 Wincc project is not integrated in scout AttachmentSimotion_wincc_flexible_communication_settings.pdf (380 Downloads) |
2/27/2020 6:11 AM | |
Joined: 5/12/2006 Last visit: 4/24/2025 Posts: 22601 Rating:
|
Hello, if you get error 14020 you must recompile the WinCC and Reload the WinCC to the Panel/RT.
Christoph |