Posts: 17 Rating:
|
Thanks Jerry - I am using 4.0 SP8. I guess I'll be getting 4.1. |
11/13/2007 10:27 PM | |
Posts: 17 Rating:
|
I have configured the PROFINET Network also. The topology is setup and it is set for IRT |
11/14/2007 5:50 AM | |
Joined: 5/12/2006 Last visit: 4/24/2025 Posts: 22624 Rating:
|
Hello, that's one big difference between 4.0.0.8 (V4.0 HF8) and V4.1. When you assuming an axis to a drive object there will no name displayed in 4.0.0.8 because there is no mecanism to tranfer the PROFIBUS Configuration data from Scout to HW- Config. In V4.0 you must configure the telegrams HW- Config and in SINAMICS Configuration Dialog from SINAMICS S120 both manually and consistency by yourself. I attach an zipped word document to show you detailed informations. Regards Christoph AttachmentDetail.zip (940 Downloads) |
11/14/2007 5:09 PM | |
Posts: 17 Rating:
|
Thanks Christoph - My question has now been answered perfectly |