5/16/2017 3:26 PM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello DGremo; The easiest way to communicate between a S7-1500 and S7-400 would be GET/PUT function blocks. Setup a network between the 2 PLCs. Decide which one will be client (the one that programs the PUT and GET functions) and which one will be server (passive partner). In Netpro create connections between the 2, and follow the detailed explanations in the following document: sample-program-get-put-with-s7-1500 Hope this helps, Daniel Chartier |
5/17/2017 4:36 PM | |
Joined: 5/15/2017 Last visit: 10/2/2020 Posts: 4 Rating:
|
Hi there! Thanks again in advance!!! Any extra data or info , just tell me! Daniel.- Attachment170517_Comm_S7-1511_and_S7-412.pdf (77 Downloads) |