Dear Hothing, for communication through ISO-on-TCP it is recommended to use LEN 0. In this case you have to define the receive-length through the Parameter DATA (e.g. P#DB10.DBX0.0 BYTE 16 or symbolic information of a struct). You can find a sample-program on https://support.automation.siemens.com/WW/llisapi.dll?aktprim=0&lang=en&referer=%2fWW%2f&func=cslib.csinfo&siteid=csius&load=treecontent&extranet=standard&viewreg=WW&nodeid0=19737445&objaction=csview Regards, yy1 |
4/22/2009 11:20 AM | |
Posts: 2 Rating: (0) |
Thanks a lot! Working. |