12/15/2012 12:06 PM | |
Posts: 14 Rating:
|
Dear Amol Don't use any siemens library, directly map I/os for Data transfer no need to use any standard block in either PLC. |
12/17/2012 6:11 AM | |
Posts: 14 Rating:
|
Thanks for your kind correction. I have made a wrong typing |
12/17/2012 12:58 PM | |
Joined: 9/27/2006 Last visit: 3/14/2025 Posts: 12344 Rating:
|
Hello Amol; I have used Anybus gateways in different projects, at different times, when required. I have always found their documentation quite informative: http://www.hms.se/upload/260-4288-Application%20Note%20PROFIBUS_NetTool_1.20.pdf This application note shows how to configure a Siemens ET 200S as a slave to the Anybus communicator, follow the step-by-step project to setup the Profibus side of the gateway. For the other network, you will need to open the Anybus manual for that bus. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/17/2012 9:47 PM |
|
This contribution was helpful to
1 thankful Users |