7/7/2019 6:17 AM | |
Joined: 12/18/2014 Last visit: 12/1/2023 Posts: 31530 Rating:
|
Where should the setpoint be passed on? As a parameter for an analog threshold switch? Perhaps enough as a statement but already this FAQ from Siemens: How can you configure references between blocks in LOGO! 8? If not, then you have to give more details (also concerning the LOGO!). |
7/7/2019 4:15 PM | |
Joined: 2/5/2015 Last visit: 9/27/2023 Posts: 127 Rating:
|
Hi ixo65 logosoft comfort 8.1 and tia portal v14.1 I’m reading a pt100 from rtd card. Showing this value on hmi tp177. It’s VM0. I have a iofield to set a temperature setpoint I want the motor to switch on, for example, 10 degrees the motor switches on. To send this information to the logo I’m using VM2 and network analog input (because this is set on hmi). The program is working ok. BUT I’m case of a power failure the temperature can’t go to zero it must hold the setpoint value adjusted before. I just don’t know how to make this last setpoint adjusted retentive on Logo. Should I write it back on vm2?! But how to do it without making a confusion in the program I created? Does this information help?! thanks. PS: I use ladder language for logo. |
7/7/2019 4:20 PM | |
Joined: 12/18/2014 Last visit: 12/1/2023 Posts: 31530 Rating:
|
Yes, the informations are helpful. I will give you an example during the afternoon. |
7/7/2019 7:34 PM | |
Joined: 12/18/2014 Last visit: 12/1/2023 Posts: 31530 Rating:
|
Sorry, I can give you only an example for the LOGO!. In my TIA V14 SP1 ther's no TP117, also not in V15.1. From the TP you write in e.g. in VW0. In the LOGO! program the setpoint linked via parameter VM mapping into the parameter V1. AttachmentSetpoint.zip (156 Downloads) |