2/9/2013 1:18 PM | |
Joined: 9/27/2006 Last visit: 5/9/2024 Posts: 12257 Rating: (2666) |
Hello Ugljesa: You can simulate network connections inside PLCSim 5.4, within limitations, if you have prepared a correct harware configuration for the simulated CPUs: From the manual for PLCSIM version 5.4: S7-PLCSIM 3.3.2 Supported communication blocks Multiple start capability of S7-PLCSIM V.5.4 with communication support between the CPUs Several CPUs can be simulated at the same time with the new function. These different CPUs can communicate with each other if an appropriate hardware configuration has been loaded beforehand. This requires unique addresses of the CPUs in the same subnet. The communication between the CPUs supports the following communication blocks: ● SFB8 "USEND", ● SFB9 "URCV", ● SFB12 "BSEND" ● SFB13 "BRCV" ● SFB15 "PUT" ● SFB14 "GET" ● SFB19 "START" ● SFB 20 "STOP" ● SFB 22 "STATUS" ● SFB 23 "USTATUS" Note S7-PLCSIM is not real-time capable. Time response constraints may occur during the communication Hope thie helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
2/11/2013 9:41 AM | |
Joined: 10/29/2012 Last visit: 3/4/2024 Posts: 102 Rating: (1) |
Thank you for your reply. |