Hello,
I made this with KTP1200 Basic PN (6AV2 123-2MB03-0AX0).
It is not possible change date and time format on basic panel in regional settings in operating system of panel.
It is necessary make some change in project in TIA Portal. Step1: In HMI alarms -> System events -> Import system events Step2: In Project texts -> System texts -> Change date and time format in selected language (Now format will be change on depend of selected language) Helpful? Rate it. :-) Thanks AttachmentDaT.zip (210 Downloads) |