Hello NICHOLAS Did you take the Upload yourself ? Can you see the DB1 in PLC Blocks Directory ?. Data Block 1 ( DB1 ) is already integrated in the programmable controller with preset values (default parameters). After performing an overall reset, you can load the default DB1 from the programmable controller into your programmer and display it on the screen. |