6/25/2012 3:48 PM | |
Posts: 767 Rating: (69) |
Hello miskopeter, The recommended branch fuses for these book size motor modules are listed byMotor Module rated currentin product catalog Siemens PM 21 2011 page 13/35. [attached is pdf] Deputy AttachmentBranch Fuses Booksize Motor Modules.pdf (561 Downloads) |
6/25/2012 4:30 PM | |
Posts: 8 Rating: (0) |
Thank you but this is for motor modules witch have separate fuses (each motor module 1 fuse) , but i need solution when you have more booksize modules on one fuse like on the picture (attached in first message). |
6/25/2012 6:17 PM | |
Hello miskopeter, I am sorry I did not understand that was what you were asking. Unfortunately, the grouping of multiple motor modules such as this is not completely documented in catalogs or manuals due to there being muliple combinations of motor modules and local codes may cause conflicts in information. In your case this can be determined by referring to the DC link current Idof the two motor modules per attachment: 60amp 72 85 amp 102 Sum equals 172 Since the sum is between 158 and 200 select the individual fuse for the DC link current Idof 200. This would be the 400 Amp fuses of 3NE1332-0 Deputy AttachmentSingle Motor Modules Technical.pdf (501 Downloads) |
