7/9/2019 8:28 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (295) |
Hello, technicalwise yes, each block (depending on the complexity) needs a certain amount of CU utilization (computation load). But to make it easier for the user there is a rule of maximum 1500 blocks calculated on one device (CU320-2) in sum (e.g. 1000 blocks at a Servo + 500 blocks at a Line Module). (see DCC programming manual) Of course the CU utilization highly depends on the selected DCC cycle times. It make a BIG difference whether the blocks are calculated in 1ms or in 32ms cycle time. The resulting utilization comes additionally to the load that is already given by the number of drive objects on the device (number of drives, cycle times for the drives, …) So a general information cannot be given as there are so many dependencies for the utilization of the CU. For example check DCC example applications like DCC synchronism...There are a lot blocks used for calculation and in the documentation you can find example utilizations for the CU for certain amount of axes. https://support.industry.siemens.com/cs/ww/en/view/109757232 |
Best regards, |
|
This contribution was helpful to1 thankful Users |
7/9/2019 8:59 AM | |
Joined: 6/22/2016 Last visit: 3/19/2024 Posts: 6 Rating: (0) |
Thanks to all. Found in the manual on Sinamics DCM in Appendix B data cycles. Page 537-541. |