Hi Skata, per the APL SP5 manual (which you can download herehttp://support.automation.siemens.com/US/view/en/48034370, see page 123) Defining startup characteristics for motors, valves and controllers Bit = 0: Starting the block in manual mode and in neutral position. With controllers, the setpoint is set to (SP_Int) internally. See also the Neutral position for motors, valves and controllers (Page 37) section for more on this. Feature bit 16, Neutral position manipulated variable takes effect at startup (Page 142), specifies travel to the neutral position Bit = 1: Starting the block with the last stored values, in other words in the last operating mode set (manual, automatic or local mode) and at the last valid position. Note Special note following complete download to the CPU Following a complete download to the CPU, the motor protection signal Trip is evaluated during the initial run as good (=1). When a motor protection signal is pending, this causes a non-struck-through message with time stamp and auxiliary values beginning with |