Hello, If you would have chosen another text, you code the hex values of the text in the array of bytes, As the comment also tells, some systems might want the TSAP to start with E0, 02, followed by some furhter ascii characters. An example: |
Best regards |
|
This contribution was helpful to
2 thankful Users |
12/31/2016 11:20 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, B#16#49 A TSAP is composed of an array of bytes, that can be text. |
Last edited by: jklm at: 12/31/2016 11:22:13 AMBest regards |
|
This contribution was helpful to
1 thankful Users |
12/31/2016 2:12 PM | |
Joined: 12/2/2010 Last visit: 4/2/2024 Posts: 61 Rating:
|
Hi, I took the sample program from the above link and I have changed the HW config. as per my Two PLCs(CPU417-4, CP443-1, CP443-1) and the same program downloaded into the PLCs. But the connection is not established and the TCON status is 7000. Could you help us to establish the communication. Thanks, Sankar AttachmentIot_Testing.zip (106 Downloads) |
Regards \ Sankar |
|
1/1/2017 2:02 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello Sankar, Just open netpro, configure a connection in ISO-on-TCP between both systems. |
Best regards |
|
This contribution was helpful to
1 thankful Users |
1/1/2017 9:07 PM | |
Joined: 12/2/2010 Last visit: 4/2/2024 Posts: 61 Rating:
|
Hi, Already I have tested with my PLC's through Netpeo using SFB14 and SFB15 and its working. Am doing this exercise to learn, if possible kindly guide me for the above testing. |
Regards \ Sankar |
|
1/2/2017 10:11 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello Sankar, For ISO-on-TCP you must use the extended The TSAPs notation, with One side must have active_est = True, the other side must have it set to false. Verify also that your CP (its FW version and model) is OK to support the open IE bloks. You need at least Firmware V5.1 on the CPU to operate CP 443-1 GX20 / GX30 / EX20 / EX30. |
Best regards |
|
This contribution was helpful to
1 thankful Users |
1/2/2017 3:31 PM | |
Joined: 12/2/2010 Last visit: 4/2/2024 Posts: 61 Rating:
|
Hi, Thank you for the continuous support. My CPU417-4 firmware is v.5.3.5 and CP443-1 firmware is V3.2.1 What is this - next_staddr_len ? Regards, Sankar |
Regards \ Sankar |
|
1/2/2017 4:52 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, next_station is not used. Set the length to 0. |
Best regards |
|