10/10/2010 2:27 PM | |
Posts: 42 Rating: (1) |
Dear experts I selected following modules on an ET200M.I considered the current consumption of each module from Backplane and the total value is less then 0.6 A. DI(15)+DO(100)+DO (110)+AI(50)+AI(50)+TC(100)+TC(100)TOTAL= 525mili ampere
Splitted from ET200 RACK BACK PLANE . |
Last edited by: ROCLIM at: 10/11/2010 3:15 PMLast edited by: ROCLIM at: 10/11/2010 3:15 PMLast edited by: O_Moderator at: 10/11/2010 10:22 AMnew subject after splitting |
|
10/12/2010 3:11 AM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
Hello ROCLIM I think you are looking at the wrong value andthere is some confusion happening between the 24V related supply currentinto the IM153-2 and it5V related backplane current supply capacity. As per IM153-2 technical spec it can draw a maximum of0.6 Ampfrom the 24V supply, out of which itcandeliver a maximumof1.5 Amp to the 5V backplane bus though (i.e. you have plenty of spare capacity with your selection). I hope this heps |
Cheers |
|
This contribution was helpful to1 thankful Users |