Hi Juan, compared to a SIMATIC S7-300/400, the SIMATIC S7-1500 (and also the S7-1200) has a different system reaction on events. Only the violation of the cycle monitor time or a programming error will cause a stop. You will find more details at 'Events and OBs' in the system manual 'STEP 7 and WinCC Engineering V17'. This manual also provides information about the different types of organization blocks. The SIMATIC ET 200SP analog input module AI 8xU BA provides a configurable diagnostics, but only per module. Therefore, you will not receive a channel diagnostics. You can verify this, using "Online & diagnostics" for the module. Kind regards |