Hello simatix assuming you do NOT use the onboard DP port of the 95U for anything you can replace a6ES5095-8ME02 (95U with onboard Profibus DP master Interface)witha 6ES5095-8MD03 (95U with onboard DP slave interface) and vice versa. If you do however use the onboard DP port of the 95U for anything, you can NOT directly replace one with the other. Having said that,you could replace a 6ES5095-8MD03 (95U with onboard DP slave interface) with a 6ES5095-8ME02 (95U with onboard Profibus DP master Interface), add a DP/DP coupler to its interface, configure the 95U for the DP/DP coupleras well as reconfigure the DP Master of the system to keep the data exchange between the two the same. And here are the links to manuals: S5-90U/S5-95U Programmable Controller System Manual SINEC L2-DP SlaveInterface on the S5-95U Programmable Controller ET 200 Distributed I/O System with IM 308-C and S5-95U (with DP Master port) I hope this helps |
Cheers |
|