2/2/2010 9:42 AM | |
Posts: 27 Rating: (1) |
Pleas explain what is the difference between Analog input module 6ES5243-1AB11 & 6ES5243-1BA11. |
2/4/2010 4:47 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Dear jkp You can download IP243 manual from the following link : http://support.automation.siemens.com/WW/view/en/1087091 Pl see section 2.2 ( Page 2-2 ) for differences between the different variants of IP243 Cheers Navnag |
There is no such thing as the last bug in a program |
|
2/4/2010 12:59 PM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Dear jkp What is the PLC Type that you have ? I Assume it is S5-135U / 155U 6ES6 243-1BA11 - Is a VERY old module ( Discontinued in 1994 ) .. Functionally it is supposed to be compatible with -1AA12 and possibly -1AA11 too !!! Somaybe the only way to find out is to actually Try ... as very little information is available on this module except this ... http://support.automation.siemens.com/WW/view/en/4138275 Good Luck Navnag |
There is no such thing as the last bug in a program |
|
2/5/2010 6:53 AM | |
Posts: 27 Rating: (1) |
Yes it is S5 155U.Please find attached pdf for phographs, its connector position is different.
AttachmentS5 Analog Input card.pdf (237 Downloads) |
2/8/2010 6:07 AM | |
Posts: 27 Rating: (1) |
Thanks Navnag, it means we have to procure spare card. |