Hello senthilrajan The main diffrence between the block related message and Symbol related message is that Block related messages Block related message depend upon the blocks that you use, type of CPU say S7 300 or S7 400 Alarm DQ or Alarm D block will work in s7 300 Alarm_8p, notify blocks will work only in S7 400 again the number of active alarm depend upon the performace parameters of the cpu, you can see this property in Siemens catalogue Symbol related message Only possible in S7 400 system Both the system is possible only via AS-OS engineering installation i have attahced a list for easy understanding Have fun... AttachmentDiff_Msg.pdf (110 Downloads) |
Last edited by: Tagolover at: 5/29/2010 11:42 AMJazz |
|
12/2/2013 1:11 PM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question splitted to creating symbol related message Best regards O_Moderator |