6/26/2013 1:37 PM | |
Posts: 72 Rating: (2) |
dearali_abc you got only SF or SF with BF ? can you check modul infomation ( block ->cup -> modul infomation (or) ctrl+d). |
6/26/2013 1:52 PM | |
Posts: 35 Rating: (0) |
thanks for reply both light are on sf on cpu and bf on et 200m module |
6/26/2013 2:02 PM | |
Joined: 4/24/2006 Last visit: 4/26/2024 Posts: 8615 Rating: (1147) |
Hello ali_abc, You are using the wrong LADDR. You should not use Profibus address, but logical address. Perhaps this link might help: how do you switch off (decouple) a slave without causing an error entry to appear in OB 86/ OB 122? Best regards, Wizard |
6/26/2013 3:46 PM | |
Posts: 35 Rating: (0) |
hello saravana kumar I have cpu 318 2dp v1.1 which can not support sfc 12 according to ur statment. so how can I disable the slave.
|
6/26/2013 3:58 PM | |
Posts: 35 Rating: (0) |
hi ste39 I not understand what u say... you mean that logical address are Input output address of et 200m??
|
Last edited by: ali_abc at: 6/26/2013 4:08 PM |
|
6/26/2013 4:20 PM | |
Joined: 2/6/2009 Last visit: 3/21/2024 Posts: 938 Rating: (118) |
Hi, Sure it won't be possible to use SFC 12 with the current firmware of the CPU 318 you have. Because the CPU's list were downloaded from the forum. Here is thelinkfor Firmware update for the CPU 318 with the deatailed procedure to the update. Please update and use the SFC 12.
|