Hi, which style are you using? Does this behavior also occur with the standard style? With best regards, Fred |
7/27/2023 6:49 AM | |
Joined: 1/21/2013 Last visit: 1/24/2025 Posts: 3462 Rating: (543)
|
Hi, Referring to an old, unresolved problem by simply saying "same here" will not improve your chances of getting a qualified answer. In WinCC Unified, most screen objects had a mouseover effect. This works fine when using a mouse, as you will always do when using PC Runtime, but it did not work well with touch input. I write "did not work well" because the problem was fixed with the V18 Update 2 image. You may not need a V18 Update 2 WinCC Unified ES installed on your PC, but you definitely need the image installed on the panel. However, I did my verification with Update 2 ES, V18.0.0.2 as the configured device version and the Update 2 image. Be careful when using the Time or LTime datatype in an IO field, Update 2 has trouble displaying the values. Siemens is working on a solution, for now it's recommended to use DATE_AND_TIME instead. Edit: Update 2 has been replaced by Update 2.1. This version should include a fix for the Time/LTime problem. Kind regards |
Last edited by: Stefan Arcularius at: 08/13/2023 09:48:23Added note about update 2.1 |
|