11/29/2017 8:59 AM | |
Joined: 9/21/2017 Last visit: 11/3/2021 Posts: 30 Rating:
|
For access to SCADA interface via WEB.Or only - RT Professional,WebNavigator and DataMonitor ?In that case. |
11/29/2017 11:03 AM | |
Joined: 12/28/2015 Last visit: 2/7/2025 Posts: 256 Rating:
|
Hello a server system is allways better for Scada Application. For example on Web Naviagtor Windows 7 maximal clients = 3. Windows Server 2012 much more than 3 client´(it depends on the wincc version therefore you must look in the instructions of the wincc version). Also you nee the CAL Licensens from Microsoft. https://www.microsoft.com/de-de/licensing/produktlizenzierung/client-access-license.aspx And an example for wincc webnaviagtor https://support.industry.siemens.com/cs/ww/de/view/28309119 |