3/14/2018 11:26 AM | |
Joined: 4/28/2015 Last visit: 10/9/2023 Posts: 394 Rating: (55)
|
Please have a look in the motion control manual on page 66... https://support.industry.siemens.com/cs/ww/en/view/109754206 Reference speed The reference speed of the drive is the speed, with which the drive spins when there is an output of 100% at the analog output. The reference speed must be configured in the drive, and transferred into the configuration of the technology object. The analog value that is output at 100% depends on the type of the analog output. As an example, for an analog output with ±10 V, the value 10 V is output at 100%. Maximum speed In this field, specify the maximum speed of the drive. The maximum speed is limited by the drive and by the value range of the analog output. In the simplest situation, the reference speed and maximum speed are identical. Analog outputs can be overloaded by approximately 17%. If the drive permits overloading, you can use this to operate an analog output as a limit in the -117% to 117% range. |
This contribution was helpful to1 thankful Users |
3/14/2018 11:34 AM | |
Posts: 2826 Rating: (682) |
You have now spared me a bunch of headaches. |
Follow us on