12/7/2018 5:50 AM | |
Joined: 9/16/2013 Last visit: 9/14/2024 Posts: 29 Rating:
|
additional information
AttachmentInfo.zip (396 Downloads) |
12/7/2018 6:01 AM | |
Joined: 9/16/2013 Last visit: 9/14/2024 Posts: 29 Rating:
|
The project on SCOUT 5.2 is attached (Servo_Setting.zip).
AttachmentServo_Setting.zip (370 Downloads) |
12/7/2018 10:08 AM | |
Joined: 9/16/2013 Last visit: 9/14/2024 Posts: 29 Rating:
|
Video files: https://drive.google.com/file/d/1HMTvkpWqQByuJ9vs4ncAH-udhEYneFcL/view |
12/7/2018 4:28 PM | |
Joined: 10/11/2006 Last visit: 4/17/2025 Posts: 6008 Rating:
|
Hello, there is an undervoltage fault. Maybe the infeed can't supply the necessary power? You can do traces about DC-Link voltage with lower speed and then with higher speed to analyze the behavior. Infeed parameter r26 ; r27; endlesstrace For further support you can do a hotlinecase. https://support.industry.siemens.com/My/ww/en/requests#createRequest |
With best regards, |
|
12/17/2018 3:49 AM | |
Joined: 9/16/2013 Last visit: 9/14/2024 Posts: 29 Rating:
|
"_LineModul_control" command helped. |