8/8/2023 6:19 AM | |
Joined: 6/26/2023 Last visit: 11/28/2023 Posts: 3 Rating:
|
I am trying to downgrade a PLC S7 1200 1214C using TIA Portal, but the "The firmware cannot be transferred. " shows the current version as v4.5.1. I need a version below 4.4. Can anyone support me in determining if downgrading is possible? If yes, please guide me on how to perform the PLC downgrade. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/08/2023 10:49:18New subject after splitting |
|
This contribution was helpful to
1 thankful Users |
8/8/2023 6:25 AM | |
Joined: 3/11/2019 Last visit: 11/29/2023 Posts: 1082 Rating:
|
Hi, no, its not possible. For the S7-1200, there was a new hardware revision in between these firmware versions. How do you load a project into an S7-1200 CPU if its firmware version cannot be selected in the hardware catalog of STEP 7 (TIA Portal)?regards sancruz |