2/7/2025 7:42 AM | |
Joined: 4/24/2006 Last visit: 4/29/2025 Posts: 8971 Rating:
|
Hello, You will have to install the Panel images. See the following link: Error when loading the project into an HMI Panel with Firmware adaption Here a link to download the images: Image Downloads for SIMATIC HMI Operator Panels: Comfort / Mobile / Basic Panels Please install the images for TIA Portal v19 And in your project, you will have to select the HMI, right mouse-click -> Change device Select the same panel, with version v17 Best regards, |
2/7/2025 3:13 PM | |
Joined: 4/24/2006 Last visit: 4/29/2025 Posts: 8971 Rating:
|
Hello, You will have to use "HMI_PIU_installer" to install the images for TIA Portal v19. Best regards, Wizard |
2/7/2025 4:03 PM | |
Joined: 1/21/2013 Last visit: 4/29/2025 Posts: 3778 Rating:
|
Hi keroo nageh, Unfortunately, the HMI Panel Image Updater (PIU) has problems logging into SIOS. So most users cannot use it at the moment (this applies to V1.0 and the current V1.1 version). So please follow the readme you can find in section 1.2 of the download page. Kind regards |
2/10/2025 7:50 AM | |
Joined: 4/24/2006 Last visit: 4/29/2025 Posts: 8971 Rating:
|
Hi, Perhaps this might help: https://support.industry.siemens.com/cs/ww/de/view/109825750 Best Regards, |
Last edited by: Moderator_Lan at: 02/10/2025 10:05:31link optimized |
|