2/7/2007 4:57 AM | |
Posts: 73 Rating: (20) |
Hello, You should find an S7200/s7300Function Block Library for diagnosing the Safety Monitor on the ASIMON software CD. Using this block all diagnostics available via the ASIMON software are now availablein the PLC program. In the past I have done a screen shot of the Safety Monitor program and imported this graphic into the HMI. Then I placed circles on the graphic in WinCCFlex and linked them to the Diagnostic Data in the DB. Based on the diag data you can display the different diag colours. Please see the attached pictures. Regards AttachmentPresentation2.zip (795 Downloads) |